Do not use current=1.0. The MSG's current is a fraction of 100 to 2800 mA, so 1.0 commands 2800 mA, more than any of the MSG's three steppers takes, and the firmware does not clamp it (known issue KI-9 of the MSG manual).

Keep current at or below:

  • 0.51 with the 21.5 mm stepper
  • 0.70 with the 40 mm stepper
  • 0.74 with the 60 mm stepper

Details: On PAROL6 and PAR6, Driving it and the known issues of the MSG manual.